Fire Alarm System for Monorail Station
What type of fire detector do you think is best for a monorail station? The monorail station consists of two storeys and a mezzanine, the station is going to be built over a crowded street.
Because the station is semi-open (above spaces are covered by roof but from sideways the station is exposed to air current), I don't think heat or smoke detector is a viable option, so I guess a flame detector suits this case, but there are many types of flame detectors and also cost is an important issue.
So, what type of detector do you suggest? If you suggest flame detector which type (UV, IR or UV/IR)
Any help is appreciated
RE: Fire Alarm System for Monorail Station
2. what is there to burn?
3. And the entire structure is open on at least one side to the atmosphere?
4. Fire sprinkler sytem to be installed?????
5. mainly steel structure???
I am looking for a general guideline, consider the conditions as they are normally are
1- yes of course
2- what is in a monorail station? paper, electric cables, plastic
3- it's semi-enclosed from each side
4- no
5- yes
What do you think of "Air Sampling Smoke Detection" for this case?
Manual system only?
Manual plus automatic??
If automatic, you could go with rate of rise heat detectors
My question is why is it required if it's outdoors?