Wind generator working like synchronous motor
Wind generator working like synchronous motor
(OP)
Dear all
We are having problems with some synchronous wind generators and we have to test like a synchronous motor, for that we will uncoupled the generator and fed the stator and rotor in order to run like synch motor and perform no load vibration test.
Some one with experience in this action? any recommendations about it? how can I know if the vibration problems come from the rotor or stator winding?
All inputs are wellcommen
Thanks and regards
Carlos
We are having problems with some synchronous wind generators and we have to test like a synchronous motor, for that we will uncoupled the generator and fed the stator and rotor in order to run like synch motor and perform no load vibration test.
Some one with experience in this action? any recommendations about it? how can I know if the vibration problems come from the rotor or stator winding?
All inputs are wellcommen
Thanks and regards
Carlos





RE: Wind generator working like synchronous motor
What "vibration problems"? Are those the "some problems", or are there other issues?
What did you measure?
Mike Halloran
Pembroke Pines, FL, USA
RE: Wind generator working like synchronous motor
Do the vibrations occur also when you pitch in the blades without generating power?
RE: Wind generator working like synchronous motor
The rotor is proper balanced, the generator is being rectified and inveted first.
Thanks
Carlos
RE: Wind generator working like synchronous motor
- Is the excitation current within limits?
- Is the generator still producing or is it completely out?
- What happens when you let the rotor spin without producing (without excitation for example?) at the same rpm as when the vibrations occur? Do you still have vibrations?
- Is the rectifier OK? When a thyristor is defect you can have similar problems but then you would have loss of power.
- What did the insulationtest show?
Best regards
RE: Wind generator working like synchronous motor