soil resistivity readings
soil resistivity readings
(OP)
im in adesert location,the on site personnel took soil resistance reading, it came back 18.3 ohms.i thought this was acceptable(below 21ohms).client wants 4ohms max.we have no bentonite,i suggest creating earth bed(soil only 1mt deep before hitting rock).daily watering and linking out earth spikes(X12) at earth bed would be suffice??






RE: soil resistivity readings
RE: soil resistivity readings
RE: soil resistivity readings
Your "Y" probe is at 50% the distance to "Z" probe, typically readings are taken at 52%, 62%, and 72% at a minimum, usually more points to verify.
You may want to do this before taking other actions.
Is this just a single rod?