Capacitor banks neutral grounding
Capacitor banks neutral grounding
(OP)
There are three cap banks (7800kVAR, 130 amps, 34.5kV) at a outdoor substation. The 34.5kV is hard neutral grounded at the transformer. They have an neutral unbalance relay that trips them off with an unbalance if the individual caps blow fuses.
Each cap bank is grounded through a PT (175/1), with the secondary of the PT's all paralleled inside the substation building going to a common over voltage relay.
The settings on the voltage relay are 8 volt to alarm and 15 volts trip with a 20-30 second delay.
My problem with this is that since the secondaries are all in parallel, wouldn't it take a lot of current on the secondary of the PT's to make the primary neutral match up on all three banks? There are no fuses on this.
Is this the proper way to do it or should there be a voltage imbalance relay for each?
Each cap bank is grounded through a PT (175/1), with the secondary of the PT's all paralleled inside the substation building going to a common over voltage relay.
The settings on the voltage relay are 8 volt to alarm and 15 volts trip with a 20-30 second delay.
My problem with this is that since the secondaries are all in parallel, wouldn't it take a lot of current on the secondary of the PT's to make the primary neutral match up on all three banks? There are no fuses on this.
Is this the proper way to do it or should there be a voltage imbalance relay for each?






RE: Capacitor banks neutral grounding
The PTs only monitor the cap neutral point voltage difference from system neutral. They do not provide a substantial path to ground. However, tying all three PTs secondaries together will produce some interesting results should one bank open one phase fuse. That bank's neutral point will head toward the center point of the two good phases. The other two banks' neutrals will stay close to the primary system neutral. The resulting PT secondaries will see high circulating current due to this imbalance. The average secondary voltage (given an open cap bank primary phase) should be sufficient to cause a trip in 20 to 30 seconds. This may fall within the PTs short time rating. Or perhaps not. Some analysis will be required.
The other case to consider is an imbalance between banks that will cause a similar PT secondary circulating current but not sufficient to cause a protection trip. Can the PTs withstand this current continuously?
RE: Capacitor banks neutral grounding
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Capacitor banks neutral grounding
RE: Capacitor banks neutral grounding
Its one PT secondary bucking another that might* over-duty them (the PTs). And as Bill pointed out, putting the secondaries in series will eliminate that problem. Separate OV relays will do so as well (for a few more $$).
RE: Capacitor banks neutral grounding
Two results;
1> Relatively heavy circulating currents, limited by the PT impedances.
2> One PT at 20 Volts in parallel with two PTs at zero volts. I would expect a resultant voltage around 7 Volts until the circulating currents blow a PT.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Capacitor banks neutral grounding
The engineer is possibly confusing parallel CT secondary windings with parallel VT secondary windings.
RE: Capacitor banks neutral grounding
RE: Capacitor banks neutral grounding
What is the impedance of a PT anyway? The trip voltage primary is 2625 volts, the other two cap banks neutral would need to be pushed off center by that same amount, while accounting for the difference in the PT impedance.
RE: Capacitor banks neutral grounding
I concluded that the PT's have a high impedance and will not cause a fire. I also conclude that the proper way of doing this is to put the PT's in series.
I am working on getting it changed. Thank you for your advice.