2 transformers/voltages, both neutrals tied to ground

2 transformers/voltages, both neutrals tied to ground

2 transformers/voltages, both neutrals tied to ground

(OP)
We have a control panel in which we'll have 2 transformers (460x115 and 460x230). The neutral of our transformers is usually wired to a 'neutral' terminal and also grounded to the backpanel. Is there any issue with both transformer neutrals being grounded to the backpanel, thus both voltages sharing the same neutral?

RE: 2 transformers/voltages, both neutrals tied to ground

Each transformer needs its own neutral conductor, but both neutrals can be bonded to the same ground point, and probably should be.  You don't want to use a ground wire as a current-carrying conductor.

If this is all inside of a control panel, you'd better check applicable UL requirements if UL labeling is required.  



 

RE: 2 transformers/voltages, both neutrals tied to ground

(OP)
ok, thank you. we plan on separating/labeling the neutrals to two different connection points, but electrically, they'll both be connected to ground. Not sure of the UL issue either, but this particular panel cannot be UL-labeled anyways, so that won't be an issue.
 

RE: 2 transformers/voltages, both neutrals tied to ground

Quote:

particular panel cannot be UL-labeled

Just as an aside - any panel can be UL-labeled if you have enough money and time.  

Cheers,

Dave

RE: 2 transformers/voltages, both neutrals tied to ground

(OP)
True. This project we are using ultrasonic generators that are only made in 230vac models and aren't UL-listed because of the leakage current, and due to that any GFCI used to allow it to be UL labeled trips when we try using it. Any suggestions that would allow us to label it would be welcome though...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources