Temperature drop on burried natural gas pipeline
Temperature drop on burried natural gas pipeline
(OP)
I am trying to plot a temperature profile along a buried natural gas pipeline. Pipe line is buried 36", Soil temp is 45F, inlet temp is 60F @ 700 psi, flow-rate is 60,000,000 scf/d (60 MMSCFD)..it is a 6" std .280" X52 FBE Durabond coated 3-5 mil thick steel pipeline, 5 miles long.





RE: Temperature drop on burried natural gas pipeline
TTFN

FAQ731-376: Eng-Tips.com Forum Policies
RE: Temperature drop on burried natural gas pipeline
- Heat exchange with surroundings
- JT effect from pressure drop
You can calculate this with high accuracy using e.g. HYSYS or a hydralic simulation tool e.g. pipeline studio. Some may consider this overkill but i think it give you certaincy with a modest effort.
Best regards
Morten
RE: Temperature drop on burried natural gas pipeline
RE: Temperature drop on burried natural gas pipeline
The way I approach this kind of problem is with a "Thermal Entry Length" which is defined as "the distance required for the dT between the fluid and the surroundings to be reduced to 20% of its original value". After the thermal entry length, heat transfer is too slow to be a practical consideration. So in the first case we reach the thermal entry length at 75.6F and in the second cast it is at 93.6F. What I found interesting is that you reach these values at around 30 miles and 50 miles respectively. These numbers are far longer than I've ever observed in the field.
I have frequently compared temperatures at meter stations on wellheads to the temperature of gas entering compressor stations less than 5 miles away. Two things I've noticed is that temperature at the compressor station is very constant winter to summer and it is constant regardless of the mix of inlet temperatures (turning large high-temperature sources on or off does not seem to affect station inlet temperature).
Far be it from me to suggest that my observations in any way trump a graduate student's manipulation of "fourth order ODE's", but I just can't buy either the lengths involved or the shape of their curves.
For the OP's situation, I would call a 60F inlet and a 45F ground temperature the same value (3% difference in absolute terms) and get on with the rest of the evaluation without a temperature profile. I do a lot of pipeline modeling and the model I use has some robust temperature modeling modules. In gas lines, turning them on or off has never made any difference at all to the recommendation that I would make about the model results. If I'm concerned about hydrate prediction then I have to turn the temperature modeling on and I have been able to explain a couple of line freezes that way, but if I model a line heater (in field gas saturated with water vapor), I get hydrate formation in the same place as the model predicted it without the heater.
David
RE: Temperature drop on burried natural gas pipeline
Hope the following discussion on the same subject will be useful: http:
"We don't believe things because they are true, things are true because we believe them."
RE: Temperature drop on burried natural gas pipeline