Pressure Relief Valves.

Pressure Relief Valves.

Pressure Relief Valves.

(OP)
I have a quick question.  I have a hydronics Rep telling me to put the pressure relief valve of a hot water system containing a heater exchanger on the suction side of the pump (right after the expansion tank).

Is this philosophy correct.  Shouldn't it be on the discharge side of the pump where the highest pressure of the system is ??

Thanks for your response.

RE: Pressure Relief Valves.

Yes. Any safety device should protect the most vulnerable piping.

RE: Pressure Relief Valves.

Why are you asking a salesman where to put a pressure relief valve? Find another Engineer where you work and ask him.

RE: Pressure Relief Valves.

(OP)
Thanks for responding.  The Rep happens to be a mechanical engineer that specializes in hydronics, pumps and hydronic accessories, and holds training seminars on such subject matters. So he is a qualified professional.

Having said that, our design showed the pressure relief valve on the discharge of the pump, but the contractor installed it on the suction side after the expansion tank.  And to my surprise this hydronics engineer agreed with the location.  My collegues at the office disagreed with the location and hence I turned to this forum for other opinions.

I wanted to see if there was a logic behind locating it there that I didn't quite understand or if anybody else agree with it.

 

RE: Pressure Relief Valves.

The expansion tank controls the basic pressure in a loop and is the point where the pressure should be fairly constant. The tank is also likely to have the lowest pressure rating of any component in the loop, so it is what you are protecting. A centrifugal pump is self limiting in terms of pressure it can create and has no need for a relief valve.

RE: Pressure Relief Valves.

Should be at the point of least pressure change in system.  

RE: Pressure Relief Valves.

Installing the pressure relief will give you a sort of false positive in the system pressure.  Pressure will be greater at that point due to the pressure added by the pump.  You always want to install the relief at the neutral point of the system with the expansion tank and air separater.  This way the relief valve will open only when the system pressure gets too high, and not the flow pressure.

RE: Pressure Relief Valves.

Pressure relief valve release the builtup static pressure for safety. If you took a look of Bernoulli's equation, the pump discharge side has highest flow pressure, but not necessary highest static pressure. I agree with Compositepro, put it at somewhere the pressure is constant(low/no flow).  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources