Panel Incomer breaker AT rating
Panel Incomer breaker AT rating
(OP)
Hello,
I have a panel connected with different types of loads like motors, lighting, sockets etc. The total load current on the panel is 135Amps. By considering the 80% loading of the breaker(135A x 1.25 = 168.75A) i need to select a breaker of size 200A.
Now what is the breaker AT rating i have to specify corresponding to my load current. How to select the breaker AT rating based on IEC/BS standards.
I have a panel connected with different types of loads like motors, lighting, sockets etc. The total load current on the panel is 135Amps. By considering the 80% loading of the breaker(135A x 1.25 = 168.75A) i need to select a breaker of size 200A.
Now what is the breaker AT rating i have to specify corresponding to my load current. How to select the breaker AT rating based on IEC/BS standards.





RE: Panel Incomer breaker AT rating
So bottom line; if you want a 200A circuit breeaker, you can use any frame that will fit in your panel that has a 200A trip unit, which means it will have a notation of XXXAF/200AT. You select the frame size to be as large and you might ever think that circuit could be expanded to. If that is totally unimportant, then size it at the smallest frame size that will have a 200AT. That will vary by supplier, could be a 200AF, 225AF, 250AF, maybe even a 400AF.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Panel Incomer breaker AT rating
Also suppose you choose 200A AT rating and 400A AF rating, in future if your load grows beyond 200A, you can just change the trip unit and your breaker will be suitable for loads upto 400A, as the frame is rated to carry 400A.