Acceptable Insulation Resistance Values for 15 kV Switchgear
Acceptable Insulation Resistance Values for 15 kV Switchgear
(OP)
We have newly acquired 15 kV Switchgear and conducted insulation resistance test in all 6 poles (1,3,5,2,4,6). However the result varied significantly when the 2-4-6 poles are tested with respect to ground. Using the 5 kV, Vanguard-Insulation Resistance Tester, the largest insulation resistance recorded for 2-4-6 poles to ground is only 600-Mega ohms. While the 1-3-5 poles to grounds are having 100 Giga ohms and above insulation resistance. Looking at the manual, no shunt resistor or PTs wer connected. Verifying it to the NETA, the insulation resistance for circuit breakers/switchgear should be at least 5 Giga-ohms at 20 deg Celsius and 5 kV dc test voltage. Based from manufacturer's manual, using 2.5 kV insulation resistance tester, the insulation resistance should be at least 50 Mega-ohms.
Are there any established standards/acceptable insulation resistance values that support the manufacturer's criteria? It seems that the criteria they are using is too small and lead us not to energize the switchgear until we get clear explanation from the manufacturer of the factors that contribute to the low resistance values.
Are there any established standards/acceptable insulation resistance values that support the manufacturer's criteria? It seems that the criteria they are using is too small and lead us not to energize the switchgear until we get clear explanation from the manufacturer of the factors that contribute to the low resistance values.






RE: Acceptable Insulation Resistance Values for 15 kV Switchgear
Have you conducted any overpotential testing such as VLF or Tan Delta?
RE: Acceptable Insulation Resistance Values for 15 kV Switchgear
RE: Acceptable Insulation Resistance Values for 15 kV Switchgear
old field guy
RE: Acceptable Insulation Resistance Values for 15 kV Switchgear
You list this as switchgear, but are refering to poles. Is this switchgear or breakers?
How about AC HyPot tests? Have you conducted?
RE: Acceptable Insulation Resistance Values for 15 kV Switchgear
Thanks for the response.
This is actually a metalclad switchgear and 8 vacuum circuit breakers were drawn out to be tested. Only insulation resistance test was conducted. Taking all each insulation resistance per pole such as pole 1-to-ground, pole 2-to-ground, pole 3-to-ground, pole 4-to-ground, pole 5-to-ground, and pole 6-to-ground. The test leads were connected to the pole and the other one to the body ground.