ACI Top of Floor Slab Tolerance
My 6 story building has top of floor slab elevations off as much as 3". Generally, the survey indicates most areas are within 1/2" but there are several locations on several floors where the top of slab elevation is up to 3" too high or low. The spec references ACI & AISC for the appropriate tolerances. Anyone know what the max is? Maybe in ACI 117?
RE: ACI Top of Floor Slab Tolerance
Manual de la Construcción con Hormigón, 3ª Ed.
Waddell, Dobrowolski
Mc Graw Hill
See attachment
Do the high points align up and down the building?
This could be tricky at the perimeter if you have floor to floor glass, or if you have brick relief attached to the slab.
Max Vertical deviation of any elements +/- 1 in (Section 4.2.2) except at edges of openings that +/- 1/2 in
Thickness of suspended slabs tolerance is -1/4 in (Section 4.5.3)
Max irregularity over the distance of 10 ft +/- 0.3% (Section 4.8.2)
I think a realistically 3/4" is a good number. 3" is so far out of a reasonable tolerance
you probably want to look at AISC tolerances.