ACI Top of Floor Slab Tolerance

ACI Top of Floor Slab Tolerance

ACI Top of Floor Slab Tolerance

(OP)
My 6 story building has top of floor slab elevations off as much as 3". Generally, the survey indicates most areas are within 1/2" but there are several locations on several floors where the top of slab elevation is up to 3" too high or low. The spec references ACI & AISC for the appropriate tolerances. Anyone know what the max is? Maybe in ACI 117?

RE: ACI Top of Floor Slab Tolerance

I believe 3/4" is the number for the top of slab elevation(prior to removal of shores).  But  sounds like you have flatness and levelness issues as well.

Do the high points align up and down the building?

This could be tricky at the perimeter if you have floor to floor glass, or if you have brick relief attached to the slab.   

RE: ACI Top of Floor Slab Tolerance

In ACI 117

Max Vertical deviation of any elements +/- 1 in (Section 4.2.2) except at edges of openings that +/- 1/2 in
Thickness of suspended slabs tolerance is -1/4 in (Section 4.5.3)
Max irregularity over the distance of 10 ft +/- 0.3% (Section 4.8.2)



 

RE: ACI Top of Floor Slab Tolerance

(OP)
I have slab on metal deck (no shoring). Would this also be 3/4"? I am most concerned about the curtainwall at the perimeter having enough vertical adjustment.

RE: ACI Top of Floor Slab Tolerance

I do not think you can apply ACI 117 tolerances to the top surface of a concrete slab on deck (there is no shoring).  Did you specify a constant thickness slab, or a level slab?  Since the whole system deflects it makes a difference.

I think a realistically 3/4" is a good number.  3" is so far out of a reasonable tolerance

RE: ACI Top of Floor Slab Tolerance

The above tolerances are from ACI, sounds like you have steel beams that were placed either high or low.  The last time I dealt with this I concluded that the top of foundations were set either high or low, the elevation change was not corrected when the columns were set, and the beams framed into the columns the only place they could, high or low at the connections.

you probably want to look at AISC tolerances.

RE: ACI Top of Floor Slab Tolerance

^^^^ it is also possible that if the high points are at columns and the low points are at mid span that you have a deflection problem.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources