VFD Controling Smaller Rated Motor
VFD Controling Smaller Rated Motor
(OP)
Is there any problems of say a 110kW motor connected to a 330kW VFD?
Your technical assistance and experience is highly appreciated.
Your technical assistance and experience is highly appreciated.






RE: VFD Controling Smaller Rated Motor
RE: VFD Controling Smaller Rated Motor
Other problems are difficult to imagine. And, if you run scalar control, the only limitation usually is in the rated current and rated power setting. If you can set these parameters correctly, there shouldn't be any problems at all.