Cable voltage drop
Cable voltage drop
Dear All,
I am trying to find out the voltage drop in a Copper cable of size less than 16sq.mm. Basically it is a 3 phase circuit & i have got the unit voltage drop mV/A/m value from BS 7671.
As all of you know the formula for voltage drop calculation is
Vd=(mV/A/m)*Length*Current/1000.
now my question is, since mine is a 3 phase circuit, should i multiply the above formula by Sqrt(3) or just use the above formula for both 1-phase circuits & 3-phase circuits.
please clarify.
please clarify.
RE: Cable voltage drop
But for phase-to-neutral you have to divide by Sqrt(3)
See:
"Electrical Installation Calculations by B.D. Jenkins BSc, CEng, FIEE and other"
http://www.andazyar.org/doc/0632064854.pdf
>A single phase load on a three phase circuit, use the tables.
>Three equal loads on the three phases, use 1.73
>A single phase line to neutral load use the line to neutral voltage and the tables. (Use 1.73 to derive the line to neutral voltage from the line to line voltage.)
Bill
"Why not the best?"
Jimmy Carter
But depends on which table we shall use in this BS.
The Table 4D4B [Column 4] it seems to be for three phase distribution cable. If we shall follow the Example 2.4 from page 38 [of the above link] we shall see how it was calculated using the Table 4D4B.
The Table 4D2B [Column 3] is for single phase cable[2 conductors], indeed.
That remember me in U.K. you have to drive on the left side...:)
Actually, the voltage drop depends on the cable and the current. We only need the voltage to calculate the percentage voltage drop.
I agree with 7anoter4 when using three phase tables for single phase. Apologies.
Bill
"Why not the best?"
Jimmy Carter
If we'll take the simplified equation DV=sqrt(3)*I*(R*cos(Fi)+X*sin(Fi)) one needs to know a lot of data.
But this is the role of a standard: to state an illogical [oversized] limit [very unpleasant some time!] in order to overcome the unknown.