2006 IBC Standpipe locations

2006 IBC Standpipe locations

2006 IBC Standpipe locations

(OP)
In the 2006 International Building Code Section 905.4 Location of Class I standpipe hose connections. Class I standpipe hose connections shall be provided in all of the following locations:

2. On each side of the wall adjacent to the exit opening of a horizontal exit.
  Exception: Where floor areas adjacent to a horizontal exit are reachable from exit stairway hose connections by a 30 foot hose stream from a nozzle attached to 100 feet of hose, a hose connection shall be required at the horizontal exit.

Can some one help clarify the this for me? I am having issues applying this piece of code...

RE: 2006 IBC Standpipe locations

06  you may have a misprint


2.   On each side of the wall adjacent to the exit opening of a horizontal exit.

Exception: Where floor areas adjacent to a horizontal exit are reachable from exit stairway hose connections by a 30-foot (9144 mm) hose stream from a nozzle attached to 100 feet (30480 mm) of hose, a hose connection shall not be required at the horizontal exit.


Not required

RE: 2006 IBC Standpipe locations

(OP)
still not following...

RE: 2006 IBC Standpipe locations

If the doors of the horizontal exit are within 130 feet of the stairway,

No hose  connection is required at the horizontal exit doors

RE: 2006 IBC Standpipe locations

Seems clear enough to me.  Horizontal exits don't necessarily require standpipes but fire escape stairways do.

Are you familiar with the difference between horizontal exits and fire escape stairways?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources