Conduit filling as per BS/IEC
(OP)
Dear All,
Could you please let me know the percentage cable filling allowed for a conduit as per BS/IEC.
Regards,
Lakshmipati
Could you please let me know the percentage cable filling allowed for a conduit as per BS/IEC.
Regards,
Lakshmipati





RE: Conduit filling as per BS/IEC
http
RE: Conduit filling as per BS/IEC
RE: Conduit filling as per BS/IEC
htt
BS 7671:2008 recommends also 40%.
RE: Conduit filling as per BS/IEC
Thanks for the answers.
7another4,
could you please let me know the section in which it is given as 40% filling.
Regards,
Lakshmipati
RE: Conduit filling as per BS/IEC
http://ww
"UK wiring regulations BS7671, recommend that the total cross sectional area of the sum of the individual cables should not exceed 40% of the cross sectional area of the conduit"
And other stated:
"BS7671-2008 provide tables for cable and conduit factors, these can be found in the current IEE On Site guide BS7671-2008 Appendix 5 Pages 117 to 120"