Variable Primary Flow Chilled Water System Sequence of Operation
2

Variable Primary Flow Chilled Water System Sequence of Operation

Variable Primary Flow Chilled Water System Sequence of Operation

(OP)
I am designing a chilled water system for an administrative building. It will have a variable primary flow (single loop) with two parallel and equally-sized air-cooled chillers with one set (2 duty, 1 stand-by) variable speed pumps.

I'm hoping that someone could lead me in finding a standard Sequence of Operation for this system. I couldn't find help from the references I currently have.

Thank you all.
 

RE: Variable Primary Flow Chilled Water System Sequence of Operation

Automated Logic has an online control specification generator that covers a wide variety of system types.  I use it quite often as a good starting point then editing it slightly for my particular need.

http://www.automatedlogic.com/guide-specification/

Andy W.

RE: Variable Primary Flow Chilled Water System Sequence of Operation

Here is a standardized sequence for a variable primary flow system. Please don't share this with anyone.

The primary pump VFD modulates to maintain loop differential pressure set point, at some point near the end of the loop. Across the supply and return loops, located somewhat near the pumps, there is a minimum flow bypass line and control valve sized for about 1/3 to 1/2 design flow. The valve will normally be closed. If, during one chiller operation, the flow through a single chiller becomes too low, as sensed by a flow meter or DP transducer across the operating chiller, the control valve will modulate to maintain minimum flow.

The DP bypass valve should be fast acting but tuned; the pump VFD should be fast acting but tuned. For chillers in parallel, each chiller isolation valve should be very slow acting.
 

RE: Variable Primary Flow Chilled Water System Sequence of Operation

(OP)
Thanks, Wareagl487 your suggestion helps a lot.

Chasbean1, you can count on me. This kind of information does not come everyday even to a seasoned designer. Thank you.  

RE: Variable Primary Flow Chilled Water System Sequence of Operation

Haha - no problem. Although you're probably looking for more detail...
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources