(OP)
I am trying to determine what ampacity to use for Marine Shipboard Cable (Type P) on 75ºC terminations governed by NEC. Cable sizes larger than 4/0 are not found in NEC 310.15(B)(16) formerly 310.16. They are similar to DLO such as 373, 444, 535, etc... Do I use the next smaller value found in the NEC table?   

RE: Marine Shipboard Cable Termination Ampacity

I think that would be an acceptably conservative approach.  You might see if the cable carries a dual rating where the second rating has a published ampacity in the NEC.  

But also see Article 110.14 in the 2011 NEC.  There are new requirements for labeling of connectors and terminations used on conductors more finely stranded than Class B.  

 

RE: Marine Shipboard Cable Termination Ampacity

(OP)
Thank you for your help.  I will review Article 110.14.

RE: Marine Shipboard Cable Termination Ampacity

I should have said there are new UL labeling requirements. The connector or termination must be UL listed for the type of wire being used.   

RE: Marine Shipboard Cable Termination Ampacity

The approach you stated is an acceptable practice used in the industry.  You could also look at the following additional standards for guidance: IEEE S-135-1 (Power Cable Ampacity Tables), IEEE 835-1994 (IEEE Standard Power Cable Ampacity Tables)and ICEA P-46-426 (Power Cable Ampacity Table).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources