I am trying to determine what ampacity to use for Marine Shipboard Cable (Type P) on 75ºC terminations governed by NEC. Cable sizes larger than 4/0 are not found in NEC 310.15(B)(16) formerly 310.16. They are similar to DLO such as 373, 444, 535, etc... Do I use the next smaller value found in the NEC table?





RE: Marine Shipboard Cable Termination Ampacity
But also see Article 110.14 in the 2011 NEC. There are new requirements for labeling of connectors and terminations used on conductors more finely stranded than Class B.