Heat Load from commercial kitchen
4

Heat Load from commercial kitchen

Heat Load from commercial kitchen

(OP)
Can anyone please advice whether to consider the heat loads which is coming under a proper Kitchen hood, while selecting the AC equipment?
 

RE: Heat Load from commercial kitchen

I do not quite understand your question.
 The convective heat loads should be taken out by the hood, there may be some radiant heat load which will not be.
 The exhaust load of the hood should be replaced by makeup air.
Whether this air is conditioned or not depends where you are in the world, and the ambient air temp.
B.E.

The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them.  Old professor

RE: Heat Load from commercial kitchen

(OP)
Thank you. My question is how would you calculate the radiant heat from the kitchen equipments to add it up to cooling load?  

RE: Heat Load from commercial kitchen

Take the surface area of the hood, the specific heat of the material, the hottest temp it will be, and use your heat transfer equations.

RE: Heat Load from commercial kitchen

ASHRAE has a table provide the heat loads of the both hooded and unhooded kitchen equipments.  

RE: Heat Load from commercial kitchen

Specific to Minnesota guidelines, but there is quite a bit of information here: http://www.mda.state.mn.us/about/divisions/~/media/Files/food/business/ventguide.ashx

As others have said, makeup air is required.  AC almost becomes a moot point.  Very difficult to effectively cool except well outside of the cookline.

It is better to have enough ideas for some of them to be wrong, than to be always right by having no ideas at all.

RE: Heat Load from commercial kitchen

As stated, I use ASHRAE guidelines to determine the heat generated by each specific piece of cooking equipment located not only under the hood, but ancillary equipment (such as refrigerators, ice machines, etc.) located in the kitchen.  One I have tabulated the heat rejection numbers, I usually apply a diversity factor of 70% to 80% to the number as all equipment will not be operating simultaneously.

Andy W.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources