I am looking to size a copper coil to cool a volume of water by 5-10 degC. I have found numerous examples for heat exchanger calculations. The volume of water does have an inlet and an outlet but it is very slow so should this be treated as a batch cooling problem (think this is how they are referred to)?
All the equations I have found require an known value that I don't have. This PDF
http:// www.access engineerin glibrary.c om/mghpdf/ 0071449396 _ar007.pdf
was helpful but I want to consider a steady state problem as I desire a constant outlet temperature from the bottom of the tank.
Any help, most appreciated. I think I just need pointing in the right direction.
I am looking to size a copper coil to cool a volume of water by 5-10 degC. I have found numerous examples for heat exchanger calculations. The volume of water does have an inlet and an outlet but it is very slow so should this be treated as a batch cooling problem (think this is how they are referred to)?
All the equations I have found require an known value that I don't have. This PDF
http://
was helpful but I want to consider a steady state problem as I desire a constant outlet temperature from the bottom of the tank.
Any help, most appreciated. I think I just need pointing in the right direction.





RE: Batch cooling with an internal coil
What value do you not know?
Call the folks at Tranter.com
RE: Batch cooling with an internal coil
RE: Batch cooling with an internal coil
Good luck,
Latexman
RE: Batch cooling with an internal coil
There will exist a volume of water at a temperature (Ta). Water will flow in at the top of the tank at Tin and out at the bottom of the tank Tout. DeltaT between inlet and outlet will be a max of 10 degC.
If Tin is always constant and I require a constant Tout; can this not be considered steady state?
RE: Batch cooling with an internal coil
"The system is transient".
Good luck,
Latexman
RE: Batch cooling with an internal coil
http://
was helpful but I want to consider a steady state problem as I desire a constant outlet temperature from the bottom of the tank"
I recognise the problem is transient but I have given an explanation for why I think it can be treated as steady state.
If this isn't possible then I am unsure how to go about solving my problem.
RE: Batch cooling with an internal coil
I think you could attack this problem two ways:.
1. Cool the hot incoming fluid on its way to the tank. Then you have a classic steady-state heat exchanger problem.
2. Treat it as though you had a steady heat input (heat load), and size the internal cooling coil to remove the required amount of heat based on the tank Tout (as a constant) and the coolant tin and tout.
Regards,
Speco
RE: Batch cooling with an internal coil
Why would I cool the fluid before it enters the tank, that is why I have got the fluid passing through the tank and why I need to size the coil to cool that delta T (load).
Am I missing something?
RE: Batch cooling with an internal coil
I meant that you could possible solve your problem either way. I didn't mean to suggest using both methods.
Speco
RE: Batch cooling with an internal coil
This is the stage I got to before becomming stumped.
RE: Batch cooling with an internal coil
It's hard to find good data for natural convection cooling. I would suggest using data for an analogous type heat exchanger. I found an average overall coefficient of 70 BTU/(hr-deg F-ft^2) for platecoil in a water-to-water cooling application. The SI equivalent is 397 W/(m^2-deg K). If this were my applcation, I would de-rate that a bit for additional safety factor. I am assuming that you have a reasonable cooling water velocity inside the coil.
This should be enough to come up with a workable solution.
Regards,
Speco
RE: Batch cooling with an internal coil
Have you got a reference for that value by any chance?
Thanks
Will
RE: Batch cooling with an internal coil
It's an overall heat transfer coefficient for cooling, using a coil in a non-agitated tank, with water on both sides. The actual range given was 70-80, by the way. I got these values from an old company that made plate coils.
Here's an online reference. Note the cast iron material for the water-to-water coefficient. It would be a bit higher for a copper coil, so I think the number I gave you looks reasonable.
http://ww
Speco
RE: Batch cooling with an internal coil
http://w
For copper coils immersed in liquids (without agitation), cold water inside coil – hot water outside coil, Perry's reports overall heat transfer coefficients in the range 105–180 Btu/(h*ft2*°F).
RE: Batch cooling with an internal coil
Heat transfer = mcp(t2-t1) for the fluid coming into and out of the tank. Ans is 418W.
Then use Q=hA(tfluid-tcoil), rearrange for A:
A=Q/(h(tfluid-tcoil)
to give me the surface area needed to satisfy the load?
RE: Batch cooling with an internal coil
and out ofthe tank. If so, yes, you can do that.If you are assuming the tank is well mixed, which is typical, the fluid coming out of the tank should be at the same temperature as the contents of the tank, so t2 = t1, right?
Good luck,
Latexman
RE: Batch cooling with an internal coil
RE: Batch cooling with an internal coil
Good luck,
Latexman
RE: Batch cooling with an internal coil
[IMG]http:/