Communication problem with Eberle
Communication problem with Eberle
(OP)
I'm working on one project where communication to RTU is by IEC103 protocol. All device working good except Voltage regulator a-eberle. Is there anyone who have experience with this type ot communication with Eberle. I can't set the address of the device, it is not visible in the menu.






RE: Communication problem with Eberle
I've already commissioned severals Eberle Voltage regulators with the IEC60870-5-103 protocol interface. For the IEC103 parameter configuration you have to use the program GenReg.
If you need some help please let me know.
Best regards
Marco