Hi All

i would like some one to help me select location of ARC & Sectionalizers on 11kV OHL and 33kV OHL.
It would be great if some one can pass me a SLD of 11kV OHL with ARC & Sectionalizers marked on it and also explain a bit of the critaria or starategy to choose the location.

regards,

RE: ARC & Sectionalizers installation

ARC being auto-recloser? Or something else?
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: ARC & Sectionalizers installation

(OP)
Yes absolutly right ARC=Autoreclosures  

RE: ARC & Sectionalizers installation

Cooper Power Systems has an extensive discussion in the book "Electrical Distribution System Protection"  I Believe this is reffered to in the FAQ Power Systems found here: http://eng-tips.com/faqs.cfm?fid=1287

You may also want to check the Cooper site and see what they have on line.  Cooper mostly references IEEE Standards.
 

RE: ARC & Sectionalizers installation

Do you have any specific questions?

RE: ARC & Sectionalizers installation

Saya88,
The positions of Sectionalizers on your SLD are ok.

I consider following factors while deciding number and location of the sectionalizers:
1). Length of line/ branch
2). No. of customers effected
3). The load effected by operation of sectionalizer on faults
4). the previous fault history (if any)

Here in UK we have industry standards known as P-2/6 (security of supply). P-2/6 gives the group demnd (MVA) that must be restored within a given period of time (e.g. If group demand is 1<load<12MW) then the group demand-1MW must be restored within 3 hours of the interruption). While designing distribution OHL circuits we use P-2/6 criteria to select the position of sectionalizers.  

musa UKPN

RE: ARC & Sectionalizers installation

(OP)
@ musa UKPN

Thanks a lot man great help, could you please send me or guide me where do i get P-2/6.

highly appriciated

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources