I recently was looking at a project where I was being asked to replace a 100HP motor. Certainly one would assume that the motor is powered by 460VAC...not so, it's 230. There are three transformers hanging on the pole. I can't explain why the original project didn't include 480 transformers.
In working with the client on this project, I've suggested that they check with the power provider to see what it would take/cost to upgrade the transformers, then we could look at utilizing a separate smaller transformer for control voltages/etc. It's a small water plant and the three transformers on the pole serve nothing else.
It will likely not be worth it at this point to change the transformers due to all other power already being set up for 230...but is there an argument for running a motor that size on 460 vs. 230, that would be convincing enough to push the issue at this opportunity?
The cost/availability of the new VFD's for this size motor is troublesome as well, in the 230V rating.
In working with the client on this project, I've suggested that they check with the power provider to see what it would take/cost to upgrade the transformers, then we could look at utilizing a separate smaller transformer for control voltages/etc. It's a small water plant and the three transformers on the pole serve nothing else.
It will likely not be worth it at this point to change the transformers due to all other power already being set up for 230...but is there an argument for running a motor that size on 460 vs. 230, that would be convincing enough to push the issue at this opportunity?
The cost/availability of the new VFD's for this size motor is troublesome as well, in the 230V rating.





RE: 100HP with 230VAC
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 100HP with 230VAC
If a switch is made from 240 V to 480 V service, you may also lose the 120 V power (assuming 240 V wild-leg delta service), so you'd have to add a small stepdown transformer to come with the 120 V power that almost certainly is needed for something.
RE: 100HP with 230VAC
RE: 100HP with 230VAC
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: 100HP with 230VAC
RE: 100HP with 230VAC
A replacement motor may well be 230:460 Volt rated.
Service equipment: This will most likely need to be changed. I have installed 480 V or 600 V rated equipment (Most often breakers but switches also) for 208 Volt service because of availability but the odds are that you will have to change the service to 480 V or 600 V rated equipment.
Add the cost of a small dry type transformer and switches or breakers for 120:240 V lighting and control.
If a motor only is needed you don't have much incentive to change the voltage.
If a VFD is needed also the economics change.
If you are concerned with the possible future cost of replacing a VFD, it may be well to consider changing the voltage when and if the VFD must be replaced.
The I2R losses will be a little less at 480 Volts but not enough less to justify an equipment change except in extreme cases.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 100HP with 230VAC
The VFD's are outdated and require replacement. The client wants a soft start bypass on the VFDs, and the availability along with pricing for these components in the 230V rated for 100HP are certainly the drive behind this exercise.
I appreciate all of the discussion.
RE: 100HP with 230VAC
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 100HP with 230VAC
Pretty common really in some critical operations. If the VFD is off line for repair, their system is probably not stiff enough to start the motors Across-the-Line to keep them running.
Jartgo,
You shouldn't have too difficult of a time finding someone to quote you on a 100HP 230V VFD, but that's typically the limit. Rockwell makes them in their PowerFlex 700 Series (they pay me to say that) but if they make them, chances are most of the other major suppliers do too. I know for a fact that Yaskawa does, I've used them in the past. Looking around though, it appears that several of the European mfrs seem to stop at 75HP, maybe that's what you observed. That's probably because elsewhere in the world they would not likely ever use 230V for something that big. Here in North America though it's actually somewhat common in the HVAC industry. A lot of commercial buildings here don't use 480V, they have very large 208Y120V systems to avoid having numerous transformers on-site for all the office loads. So when they have a few large fan and pump motors, they just put up with using 230V.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: 100HP with 230VAC
Yours
Bill
Bill
--------------------
"Why not the best?"
Jimmy Carter