Singel Phase Operating Conditon for a 3-Phase Transformer
Singel Phase Operating Conditon for a 3-Phase Transformer
(OP)
A client's RFP specifies that the "480 Volt Secondary unit substation shall be rated to supply the total 480 volt auxiliary load plus 20 percent under all single Phase Operating Conditions."
How do we size/specify the transformer to continue carrying three-phase loads when the primary is single phased? The "Single Phase Condition" is not defined. We assume it refers to the primary side and not loss of one phase of 480V.
The motor loads will help maintain the lost phase, but I am having difficulty determining the benefit of oversizing a transformer to help a condition that is going to be detrimental to the plant loads.
Any ideas on why this is specified or how to comply?
These are standard delta-wye transformers feeding mostly 3-phase motor loads. Upstream is all circuit breakers and switchgear to the generator bus, no fused switches to create single phase conditons.
How do we size/specify the transformer to continue carrying three-phase loads when the primary is single phased? The "Single Phase Condition" is not defined. We assume it refers to the primary side and not loss of one phase of 480V.
The motor loads will help maintain the lost phase, but I am having difficulty determining the benefit of oversizing a transformer to help a condition that is going to be detrimental to the plant loads.
Any ideas on why this is specified or how to comply?
These are standard delta-wye transformers feeding mostly 3-phase motor loads. Upstream is all circuit breakers and switchgear to the generator bus, no fused switches to create single phase conditons.






RE: Singel Phase Operating Conditon for a 3-Phase Transformer
RE: Singel Phase Operating Conditon for a 3-Phase Transformer
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Singel Phase Operating Conditon for a 3-Phase Transformer
RE: Singel Phase Operating Conditon for a 3-Phase Transformer
RE: Singel Phase Operating Conditon for a 3-Phase Transformer
Generally, an accidental break (on the secondary of the transformer) on a supply line to motors will raise the current on the remaining motor lines by as much 200% of the normal three-phase amps (1.732X but can reach 2X due to power factor changes). OTOH, a single-phasing on the primary of the supply transformer (wye-delta or delta-wye) can raise the motor current on the secondary phase by about 230%.
BTW, single-phasing is an abnormality and you are supposed to prevent those things from happening. Motors don't work well under single-phasing.