Hi everyone,
 I have seen Liquidtite (LFMC)type EF hanging from a j-boxs vertically in the ceiling down to peices of equipment in Industrial plants. Some are up to 30 ft long. Just doesn't seem secure or good practice. I know the 2005 code states in article 350.10 shall be permitted to be used in exposed areas. (1)Where conditions of installation , operation, or Maint. require flexibility. In article 350.30 it state LFMC must be secure 12" from termination and at least every 4ft.
 They look to be in violation of article 350.30. Are there any other violations in hanging Liquidtite vertically from the ceiling?

Thanks
tpmc

RE: Liquidtite hanging from a j-box in the ceiling to peice of equipment

30 ft free riser it cannot be permitted even for 3" and more steel rigid conduit since per NEC art.344.30B(3) or Table 344.30.B(2) the maximum vertical distance between supports it is 20 ft. So for 30 ft one has to build a support tower of 10 ft tall, at least.  

RE: Liquidtite hanging from a j-box in the ceiling to peice of equipment

Hubbell has Kellems Grip made specifically for Liquidtight flex.  This could alleviate some concerns.  But a 30' drop is probably an NEC violation.  I would also be concerned about getting the weight of the conductors off the upper terminations for a 30 foot drop.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources