Retaining Wall Vehicle Guard?

Retaining Wall Vehicle Guard?

Retaining Wall Vehicle Guard?

(OP)
I have a project where I need to design a retaining wall for a shopping plaza entrance (there appears to be a river at the front of the plaza that needs to be crossed with a culvert by others).  When designing the wall I am going to apply the AASHTO surcharge on the wall equal to 2' of earth to simulate the traffic loading.  The project doesn't really fall under the AASHTO requirements as this is a private project.

My question is in regards to vehicle guards.  Does the force from the vehicle guards need to be included in the design of the wall (together with the surcharge load) or does the AASHTO surcharge already account for this load?  If so, would you use the full 10k load applied to the vehicle guard (as we should not have vehicles moving at 65mph coming into the plaza)?
 

RE: Retaining Wall Vehicle Guard?

No, add the impact 10K on top of the surcharge.  Yes, I would design for the full 10K load upon entrance unless I restricted trucks from using the road.

RE: Retaining Wall Vehicle Guard?

A couple of things to consider:

I would apply both at the same time. But it sounds like you could use IBC guardrail load (I believe 6kips) this may be more applicable. You should be able to distribute the load out over a certain length of wall. I've also wondered if you could increase your allowable soil bearing pressure by 1/3rd for short term loading condition.

Also I'm assuming this is not a segmental wall, as the guardrail design is prescriptive in this case.

EIT

RE: Retaining Wall Vehicle Guard?

(OP)
RFreund

By segmented wall you mean a modular block wall?  The wall is to be a CIP concrete retaining wall.
 

RE: Retaining Wall Vehicle Guard?

RFreund - 6K is for passenger vehicles only.  IBC (2006) shoots you off to find your own way when there are trucks involved.  Hence the use of the AASHTO prescribed 10K.

RE: Retaining Wall Vehicle Guard?

ahh, good save.

EIT

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources