control valve seat leakage pressure

control valve seat leakage pressure

control valve seat leakage pressure

(OP)
I have control valve size 3" X 300# class VI,
what should be its seat tightness pressure and body test pressure.
please know me as earliest as possible

RE: control valve seat leakage pressure



Whatever the end user specifies. (Ask to what test regulation/papers. Generally to qualify on the market: after the valve specifications the valve is produced to)

RE: control valve seat leakage pressure

ashishgaud,
    when I hear "Class VI", I imply that FCI 70-2 (or equivalent IEC 60534-4) standard is applicable, as this is the one which defines the Tightness Classes for Control Valves (but of course - as gerhardl's post suggests - You should check with Your Customer if this is true in the specific case...).    

    According to that standard, for "Class VI" seat testing the pressure "shall be the maximum rated differential pressure across the valve plug or 3.5 bar (50 psi) whichever is the least", applied with "air or nitrogen gas at 10°÷52°C (50°÷125°F)".   


    For body shell test, the usual general rules of industrial valve testing (according to the most common standards, like API 598, ISO 5208, EN 12266-1, etc..) should apply...



Hope this helps,
                    'NGL
_____________________________________  

RE: control valve seat leakage pressure

I agree with anegri and would add to look at ASME B16.34 (para. 7.2 which states in part, not less than 110% of the 100F rating, or a gas test at not less than 80psi. (You need to read the entire section.)

RE: control valve seat leakage pressure

anegri pinpointed the exact practice which most of manufacturers use. Class VI is for the soft seated valve whereas Class V is for the metal seated valve. Most buyers don't care about this though.

RE: control valve seat leakage pressure

Please let me know if the same leakage standard is applicable for on-off type butterfly valve

RE: control valve seat leakage pressure

Ask the valve manufacturer.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources