Powerflex 40P VFD - Opto output parameter

Powerflex 40P VFD - Opto output parameter

Powerflex 40P VFD - Opto output parameter

(OP)
I am using Powerflex 40P drive. I tied the opto output on the VFD terminal (pin 18) to PLC input. I used Drive explorer software to set the VFD parameter A061 (Opto Output selection) = "Motor Running". But when the motor is running, I don't see this output turn ON. Any ideas why? See attached picture.

Sriram

 

RE: Powerflex 40P VFD - Opto output parameter

The Opto outputs on a PowerFlex 40P are NPN transistors, so they are considered a "sinking" output.

Look carefully at the wiring diagram for the PowerFlex 40P and you'll see that the Opto outputs are usually used to run a brake relay and that +24V is applied to the "Output" pins 17 or 18, and DC common is connected to the Opto Common pin.

Your PLC input needs to be a "sourcing" type to use it with the PowerFlex 40P opto outputs.

This is based only on my reading of the publications;  I have not made such a connection myself.

RE: Powerflex 40P VFD - Opto output parameter

(OP)
There is a DIP switch on the VFD to choose between "Sinking" and "Sourcing".

RE: Powerflex 40P VFD - Opto output parameter

The Sinking/Sourcing slider switch affects the Digital Inputs on the drive, not the Opto Outputs.

This is illustrated in the Control Wiring Block Diagram on page 1-15 of the PowerFlex 40P User Manual, Publication 22D-UM001.

As far as I can tell, the Opto Outputs are always a "Sinking Output", so if hooked to a PLC they would require a "Sourcing Input".

An interposing relay would be a simple way to work around this issue if you have only Sinking Inputs available.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources