Over Voltage on The Other Two Phases...

Over Voltage on The Other Two Phases...

Over Voltage on The Other Two Phases...

(OP)
In case of phase to ground short circuit, will we experience a case of over voltage on the other two phase in a specific earthing system? Please elaborate.

Elecme

RE: Over Voltage on The Other Two Phases...

An ungrounded three-phase system will normally float (as a result of capacitances and possible instruement transformers) in a balanced manner with respect to ground.  That means voltage with respect to ground is VLL/sqrt(3).  
If you get a ground on one phase which is not immeidately removed by protective relaying, the other phases will rise to VLL above ground.  

Draw an equilateral triangle representing the three phases.  In the unfaulted case, ground lies in the center of the triangle.

In the case of ground fault, ground moves toward one corner of the triangle... distance from ground to the other corners is longer.

RE: Over Voltage on The Other Two Phases...


Add that in an oscillatory or resonant condition, the "neutral" may be Displaced Outside the ø-ø voltage triangle.  
  

RE: Over Voltage on The Other Two Phases...

Suggestion: The previous posting suggests that there is a dc offset with a decrement involved. These are of transient nature. If the fault is remote from the source, then the dc ofset is small. If the fault is close to the source then the dc offset is high.
See W.D. Stevenson Jr "Elements of Power System Analysis," 3rd Ed., McGraw-Hill Book Company, 1975, Chapter 11 Symmetrical Three-Phase Faults on Synchronous Machines.
Equation 11.1
Vmax sin(wt + alfa)=Ri + Ldi/dt
The di/dt will cause the higher voltage.

RE: Over Voltage on The Other Two Phases...

See:

Thread238-3370  High Resistance Grounding  

Thread238-6870  Alarm system for 480V ungrounded systems  
    

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources