schnieder sepam experts
schnieder sepam experts
(OP)
sepam 1000+ M20
After restating the sepam(power off & on),sepam goes to (failure safe mode) showing failure code 1(Majer fault) and wouldn't comes back any more.
This problme happend with many of our sepams in site.
Could we restore it back? And what is each failure code mean?
Plz help!?
After restating the sepam(power off & on),sepam goes to (failure safe mode) showing failure code 1(Majer fault) and wouldn't comes back any more.
This problme happend with many of our sepams in site.
Could we restore it back? And what is each failure code mean?
Plz help!?






RE: schnieder sepam experts
RE: schnieder sepam experts
telecontrol in / out switching operation of relay functions occurs
during an active A/R sequence. The relay crashes completely and doesn't send an alarm, so basically you lose all protection. It does reboot manually OK. I don't know whether the Sepam 1000 is similarly afflicted, but we have made the decision to replace all our Sepam relays.
Regards
Marmite
RE: schnieder sepam experts
Regards.
RE: schnieder sepam experts