Testing Short Time Pickup

Testing Short Time Pickup

Testing Short Time Pickup

(OP)
I am looking for advice on a methode for Primary Injection testing Short Time pickup on LV Power Circuit Breakers.  I am well informed on all other Primary Injections tests on Circuit Breakers, including short time delay, but am having a hard time finding information on short time pickup.       

RE: Testing Short Time Pickup

I would say that depends on the test equipment you have available and the trip units you are testing.

If you have some kind of modern test set, where you can control the pulse length, set the fault time to be longer than the STD, but a lower magnitude than the INST PU. Ramp up into the STPU level. Assuming the trip unit has some kind of LED for ST PU, that is an indication.

Most of the rest of it is similar to other primary tests

  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources