Heating Room Calculation
Heating Room Calculation
(OP)
hi guys,
looking for some help double checking my calculation.
i want to heat a room in the Plant to 130F (sterilization process). The temp of surrounding rooms is 70F. If my room dimensions are LxWxH = 178'x69'x20', the cubic volume of my room is 245,640.
Delta T=60F
We know 1 BTU is sufficient to heat 55cu.ft of air by 1F.
I've calculated 21.8 BTU/sq.ft is required. However, I'm not sure how to calculate the BTU/HR required (I calculated a really large value that seems ridiculous) so that I can spec out & purchase the appropriate electrical heaters to accomplish the job.
Any help is appreciated...
looking for some help double checking my calculation.
i want to heat a room in the Plant to 130F (sterilization process). The temp of surrounding rooms is 70F. If my room dimensions are LxWxH = 178'x69'x20', the cubic volume of my room is 245,640.
Delta T=60F
We know 1 BTU is sufficient to heat 55cu.ft of air by 1F.
I've calculated 21.8 BTU/sq.ft is required. However, I'm not sure how to calculate the BTU/HR required (I calculated a really large value that seems ridiculous) so that I can spec out & purchase the appropriate electrical heaters to accomplish the job.
Any help is appreciated...





RE: Heating Room Calculation
And, don't forget that as you heat it up, there will be thermal losses to the surroundings that the heater must also supply.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize
RE: Heating Room Calculation
within a couple hours would be ideal.
RE: Heating Room Calculation
The heat loss thru the structure will be in BTU/HR; Heat requirement for infiltration can be done by knowing some constants or by estimating the mass flow rate of the air and the result will be in BTU/HR; the heat requirement to sterilize will require a time element to determine the rate of temperature rise in the items in order to get BTU/HR during the batching process and for continuous process mass rate of the items to be sterilized will be required for a BTU/HR determination.
RE: Heating Room Calculation
I understand the info you're requesting, but don't have all of it. Can't I simplify this down and just make some assumptions? I found a site online Heater Shop that provides a BTU calculator.....It's calculating 4,605,750 BTU/HR based on the information I originally stated. That's seems HUGE! Then again, the volume of the room is quite large!.......
RE: Heating Room Calculation