Half Wave Rectification Verse Full Wave in an System
Half Wave Rectification Verse Full Wave in an System
(OP)
Can anybody explain the different on what the required power from 3 phase L-L voltage of 115VAC generator using a half or full rectification to a 3KW load?





RE: Half Wave Rectification Verse Full Wave in an System
Cheers
Greg Locock
New here? Try reading these, they might help FAQ731-376: Eng-Tips.com Forum Policies http://eng-tips.com/market.cfm?
RE: Half Wave Rectification Verse Full Wave in an System
Half-wave rectification will introduce DC into the machine winding which is almost guaranteed to cause problems because the magnetic core will saturate. Don't do it.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Half Wave Rectification Verse Full Wave in an System
Otherwise, I don't mind if it is half full or whatever.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Half Wave Rectification Verse Full Wave in an System
It is an interesting coincidence that Scotty and I said essentially the same thing at exactly the same time.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Half Wave Rectification Verse Full Wave in an System
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Half Wave Rectification Verse Full Wave in an System
RE: Half Wave Rectification Verse Full Wave in an System
TTFN