×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Exhaust Fan and Actuator

Exhaust Fan and Actuator

Exhaust Fan and Actuator

(OP)
We just replaced an existing dishwasher exhaust fan (utility set) with an uplast 2500CFM at 3.5" ESP.  We installed a motor operated damper in the curb adapter so when the fan starts up the damper opens up.  This was an internal mounted fast acting actuator 120V.  Since the owner wanted to use existing electrical and not run any new circuits (cost), we pulled 480/3/60 from the disconnect to a transformer (Nema 4) and then 120V from the transformer to actuator.  The owner wants the actuator on the curb exterior, not a big deal find an actuator with nema 4 enclosure.  Well I cannot find a Nema actuator that is fast acting, the quickest is a 75s run time.  Now besides ordering the actuator with an auxillary switch and putting in a relay prior to the fan starter so when they turn on the fan it will not start till damper is open.

Anyways would it be fine if I use a 75s run time actuator?  So when fan turns on the actuator starts opening the damper.  Will this "hurt" the fan or motor?  The factory initially sent it with a 25s fast acting actuator with no auxillary.  Thanks!  

RE: Exhaust Fan and Actuator

Probably won't hurt anything.

Might be noisy as heck when the damper first cracks open.

RE: Exhaust Fan and Actuator

Why do you need a motorized damper in the first place?
 Are you trying to avoid wind rattle from airblast/gravity operated dampers?
B.E.

The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them.  Old professor

RE: Exhaust Fan and Actuator

(OP)
We are trying to reduce the system static pressure.  What happened the engineer who designed the system designed for half the CFM required.  After the building was commissioned and the dishwasher had been running for a while they realized that the engineer sized the system for not enough CFM.  So in order to get the CFM needed in the size duct that was installed the static pressure is around 3.5" so in order to use an upblast fan (owner request) we had to do everything we could to reduce the system static pressure without removing duct in the building.  So we chose not to use a BDD.  It would have been the easiest solution but would not  been able to get the performance we needed out of the fan.  The fan is running great and at the CFM needed.  The damper is wired opened until we get a new actuator.  Thanks!

RE: Exhaust Fan and Actuator

Have you checked the pressure drop of a backdraft damper vs the motorized damper? I did a quick check and those I checked are about the same.

Backdraft damper has the advantage of not failing so often as a motorized damper, especially in a wet environment, nema 4 enclosure or not.

RE: Exhaust Fan and Actuator

(OP)
The size duct we have the damper in there is min pressure drop as opposed to the BDD.  I do not recall what the difference was but significant enough.  Normally we just install BDD that is what was on the existing fan, but for this case a MOD was used.  Thanks!   

RE: Exhaust Fan and Actuator

I need your in/lbs for the actuator and I can help you. You may or may not like my solutions but I have a few as we ran into this problem this year with a highly corrosive application (water treatment plant beside the ocean).

I also took pictures of what we did so I can send them to you.

RE: Exhaust Fan and Actuator

Put in a goose neck instead.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources