Grounding ATS for Entire Bldg

Grounding ATS for Entire Bldg

Grounding ATS for Entire Bldg

(OP)
Adding a generator to serve the entire load of a building.  The intent is to intercept the underground service (multiple sets of 3 hots & grounded neutral in PVC ductbank) between the utility padmount transformer and the switchboard inside the building and install an ATS oudoors.  This ATS will have a weatherproof enclosure and an integral breaker on the normal side.  Does the ATS now become a "service", requiring the neutral to be connected to ground at this point?  If so, then the existing service conductors now are lacking a separate ground wire and not practical to add one.  Or, can the "service point" still be considered to be in the existing switchboard allowing the 4 wire service to remain as is and having no neutral to ground connection at the ATS.  The existing switchboard is 480Y/277V and over 1000A so it does have GFP on main breaker.

RE: Grounding ATS for Entire Bldg

Nope, your new ATS is your new service.  Anyway it is if the NEC is your governing code.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources