Being new to the electrical distribution industry, I was stumped by a situation found at one of our sites.

We have a 3 phase 600/347V bus fed by a 4 wire feeder cable.  We have several loads off the bus being 600V MCCs (no 347V loads) and 600/347V Panelboards.

In one of the MCCs, there are two parallel feeder cables that are 3C with a cable ground wire (not a neutral).  The MCC is also bonded to our system ground through a separate bonding cable.

Do the feeder cable ground wires need to be terminated on both ends, or just on the feeder side?

I'm following CEC standards.

Thank you in advance

RE: MCC Feeder Cable Grounding

Both ends.  

RE: MCC Feeder Cable Grounding

(OP)
Why is that?  Would it possibly establish ground loop currents?

RE: MCC Feeder Cable Grounding

Why do you think the ground wire is there? The main purpose is to provide a fault return path and to maintain the same ground potential at each end.  

 

RE: MCC Feeder Cable Grounding

(OP)
Thank you for the advice.

The original contractor (2 years ago), installed this and turned it over as inspected and commissioned.  They also cut the grounding cables too short to reach the ground bar inside the MCC, so they are currently hanging free in the wireway.

We had an electrician in to do extend the grounding cables and terminate them onto the ground bar, but he objected claiming that it could cause a ground loop current and could damage a VFD in the MCC.

It didn't make any sense to me, but I wanted to get some feedback before I advise any action.

Is there any situation that you wouldn't terminate this wire?

RE: MCC Feeder Cable Grounding

Not terminating the ground wire at the source is a major NEC violation - I assume it is in Canada as well.  

Having said that, if these circuit are in steel conduit, it can meet code requirements for an equipment grounding conductor if approved fittings are used.  This is not as good as ground wire inside the conduit, but it would meet Code (again, the NEC).


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources