Kitchen Exhaust fan duct sizing
How do I size the duct for an exhaust fan with 1450 cfm and 1,324 rpm.
RE: Kitchen Exhaust fan duct sizing
Are you talking residential kitchen or commercial kitchen?
Fans have a performance curve that defines cfm vs. external pressure drop.
Step 1:  Find this curve for your fan.
Step 2:  Decide how many cfm you need, and use the curve to identify the corresponding allowed external pressure drop.
Step 3:  Size the duct for that pressure drop at the required cfm.
marthab,
This isn't an exhaust hood over a cooking appliance, is it?  If so, you'll have to also consider keeping the velocity of the air high enough to entrain the particulates and grease.  If not a kitchen application, listen to MintJulep.
Good on ya,
Goober Dave
Marthab
I do not know where you live, but here is a PDF of the code guidelines where I live. Most states are not that much different.
 Pay attention to page 10.
B.E.
http://www.sdcounty.ca.gov/deh/food/pdf/publications_ventilationguideline.pdf
The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them.  Old professor
Find and employ  a Mechanical engineer and don't try to bootstrap this.
Berkshire
I am surprised that NFPA 96 is not part of the listed standards governing the design and installation of kitchen exhaust systems in your neck of the wood.
Also: NFPA 96 allows lower velocities as low as 500 FPM nowadays for some specific applications such as Melink control systems.
It is and the guidelines mention it.
B.E.