(OP)
Our shop has 240 3 ph 60 Hz, and we need to run a short term (several 5 minute tests) on some equipment needing 480 3 ph.  

We have a disconnected distribution transformer, 480 Y / 240 delta 150 A secondary, which is at least 30 times the ampacity needed for the test.  

Is it OK to backfeed 240 into this to obtain the 480??

Thanks in advance!

RE: Short term step up

Yes, but there are various code rules that would have to be complied with.

RE: Short term step up

Your initial current inrush may be over 1000 Amps. You may need dual element fuses to get this energized.
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources