Difference between flow meter and storage tank level raise
(OP)
Hi Als,
Our refinery facing a problem in Reformer Flow meter and Storage tank level raising?
Storage tank level raise is +2m^3 around while flow meter is temperature compensated.
Feed inlet flow meter is not temperature compensated.
can you please explain this problem why this difference is coming in flow meter and tank level while both FT and LT is calibrated and calibration parameters also OK.
Thanks
10815L
Our refinery facing a problem in Reformer Flow meter and Storage tank level raising?
Storage tank level raise is +2m^3 around while flow meter is temperature compensated.
Feed inlet flow meter is not temperature compensated.
can you please explain this problem why this difference is coming in flow meter and tank level while both FT and LT is calibrated and calibration parameters also OK.
Thanks
10815L





RE: Difference between flow meter and storage tank level raise
What the heck does
even mean?
David
RE: Difference between flow meter and storage tank level raise
Flow meter to storage tank is indicating less flow as compare to storage tanks Level transmeter and tank calibration for total volume.
Flow transmeter to storage is temperature compensated while Reformar unit feed inlet transmeter is not temperature compensated.
The problem is Reformate to storage is going less and volume rais is more in storage tank.
Hope you will come up with some solutions.
10815L
RE: Difference between flow meter and storage tank level raise
This is an engineering problem. Those tend to be kind of difficult to solve with broad generalities and confusing language. Solutions usually require data.
David
RE: Difference between flow meter and storage tank level raise
Is the temperature significantly different to ambient?
JMW
www.ViscoAnalyser.com
RE: Difference between flow meter and storage tank level raise
Rarely are you going to get three meters to agree exactly over any useful time period. You need to decide which of the three meters is your primary device, usually based on billing and revenue objectives, make it the most accurate and calibrate it often. The other meters are indicative only.
RE: Difference between flow meter and storage tank level raise
This Refinery in middle east, difference is coming hourly basis not per day basis.
Reformate temperature line temperature is maintained 40^0C and Tank temperature is around 40^0C.
Flow transmeter is Honeywell smart transmeter. Ambient temperature difference is about 15^0C day and night.
The density of reformate is 0.82
Thanks
10815L
RE: Difference between flow meter and storage tank level raise
* Flow rates
* Flow meter type (orifice, coriolis, ultrasonic...)
* Tank dimensions
Matt
RE: Difference between flow meter and storage tank level raise
Flow is in M^3/hr (Feed is 70 and Reformate is 56m^3/hr and LPG is 2m^3/hr)
Flow meter is orfice type.
Tank dimensions no information.
You can guss it and give some input.
Thanks
10815L
RE: Difference between flow meter and storage tank level raise
Matt
RE: Difference between flow meter and storage tank level raise
Could you please provide error margin reference.
Thanks
10815L
RE: Difference between flow meter and storage tank level raise
I'd start with Liptak, Process Measurement and Analysis.
Matt