Hi all,

Been asked to look at a project of using a gas PCV isstead of a  failed water LCV...

I would presume no straight away due to differing characteristics however I have been asked to look at the Cv...

Gas valve has Cv of 100.4 where as the original water valve has Cv of 393...

would this be able to be used?

RE: Valve Cv

If that valve's Cv will pass the flow you require, then yes, if it won't, well, that is an easy no.

rmw

RE: Valve Cv

No.  The density of gas is 100 times lighter than water, so you will get 100 times the flow at the same %open.  You will be working the water valve at the almost closed position where you will have virutally no control range left to work with.  You need a valve that you can position between 30 and 70% open at set point flows.

Only put off until tomorrow what you are willing to die having left undone. - Pablo Picasso

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources