If I have a value of 500MVA on a bus, does it means its available 3-phase short circuit MVA from utility? If yes, how I can calculate Line to Ground MVA from this.
Thanks in advance
Thanks in advance
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: 3-phase MVA
Available short circuit current is usually reported in kA.
Be aware that the available short circuit current is not the same as the maximum possible fault current.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 3-phase MVA
Your info is a bit scarce to go by. Did the utility state that the threephase fault level at the bus is 500MVA? If so then by that is usually mean that a solid threephase fault at the bus will yield a fault level of 500MVA = sqrt(3)*VL*IF.
VL = line voltage (you will need to find out from the utility (or whoever your source is)what value of voltage was used. Sometime 1p.u. or sometimes 1.1p.u. is used, etc.
IF = short circuit current.
I'm afraid you cannot conclusively say what the eartfault current will be as that depends on the system earthing. If you assume solid earthing (which is most likely the case with most HV systems > 66kV) then then EF current is in the same order as the threephase current but the MVA level will be one third, i.e. 167MVA. If < 66kV I would be way of making this assumption.
Best is to get these values from your source.
Regards.