I am designing a small WWTP flow monitoring building. The floor of the flume is about 6' below the water table. I am looking for advice on what type of proprietary joint sealer to use between the footings and walls. What I have been looking at is a 6" PVC Dumbell water stop. This seems to be an appropriate method to use for preventing groundwater from penetrating the building. Just for information purposes, the portion of the building which is below the water table is only 11'-4" x 5'-8" in plan. Thanks all in advance and have a good weekend!
I am designing a small WWTP flow monitoring building. The floor of the flume is about 6' below the water table. I am looking for advice on what type of proprietary joint sealer to use between the footings and walls. What I have been looking at is a 6" PVC Dumbell water stop. This seems to be an appropriate method to use for preventing groundwater from penetrating the building. Just for information purposes, the portion of the building which is below the water table is only 11'-4" x 5'-8" in plan. Thanks all in advance and have a good weekend!






RE: Footing/Wall Joint Sealer
As an aside - We recently had a similar situation: A cellar floor about five feet below water table. We have proposed waterproofing under the cellar slab and on the cellar walls in addition to the waterstops at the wall / footing joint. Also the cellar slab was designed as a structural slab anchored to the exterior and interior footings with reinforcing both on the top and the bottom.
RE: Footing/Wall Joint Sealer
Use a 3/8 inch thick PVC waterstop, without tapering, like Greenstreak #679. Note that there a lot of details involved with waterstops, including starter walls, tieing the waterstop to the reinforcing, etc. that are vital to provide a tight joint. you might want to research some previous designs for these details.
RE: Footing/Wall Joint Sealer
http://1
RE: Footing/Wall Joint Sealer