Automatic Rollover Between Two Different Voltages

Automatic Rollover Between Two Different Voltages

Automatic Rollover Between Two Different Voltages

(OP)
A customer is requesting for backup feed from another circuit to feed their facility in the event of a sustained outage. This entails installing an automatic open transition rollover switch tying two circuits together. If their primary service goes out, then the switch will automatically rollover the service to the second circuit.

The customer is fed from a 12 kV circuit and the closest adjacent circuit is 35 kV.  To reduce cost in extending a 12 kV circuit for the second feed, it was suggested to provide rollover service between 12 and 35 kV.  I heard this can cause circulating currents on the secondary side of the substation tranformers but not sure how.  Or there any other reasons for concern with this proposal?  

RE: Automatic Rollover Between Two Different Voltages

The problem will likely be with using the wrong voltage not circulating currents.
I suspect that you are missing a transformer somewhere (35/12 kV)
Circulating current might happen when you parallel 2 transformers. In your case it is a simple transfer switch and you want to disconnect from the faulty line before reconnecting to the other.

 

RE: Automatic Rollover Between Two Different Voltages

Connect a load expecting 12kV to a 35kV supply and things will get interesting. If truly an open transition switch there can be no circulation currents.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.