What does it mean exactly and in details:
Vector Group Dd11.75 d0.75 and
Dd0.25d11.25.
Thanks
 

RE: Phase shift transformers

Your question is a bit vague, but a PST does just that.  It is used for power flow control.  SEL has a nice application paper explaining the nuts and bolts of the design and operation.

RE: Phase shift transformers

(OP)
Sorry
These transformers (double secondary each) feed VFDs and provide harmonic mitigation.
The first one gets +7.5º and the second -7.5º.
This means 24 pulses for harmonic cancellation, I suppose.
I would like to know the meaning of numbering 11.75, 0.75, 0.25...
Thanks again

RE: Phase shift transformers

electrolitic,

11.75 means 11h 45 minutes
0.25  means 12h 15 minutes
0.75  means 12h 45 minutes

on phasor diagram representig as clock (12h is zero degree)

Milovan Milosevic

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources