I have new W-beam lintel sits on existing unreinforced masonry wall. reaction is 10 kip. What is allowable bearing stress for URM. Wall is 6in thick. Do i have to use same 0.25f'm.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: masonry stress
If it is not specially inspected, then you are only allowed half that value. Sounds like you're in this range to me.
Mike McCann
MMC Engineering