Regarding NFPA 13 2010, 9.3.6 Restraint of Branch Lines. I have a few questions.

If you are working with branch lines attached at both ends by a main (grid) which is restrained laterally and longitudinally by sway bracing in accordance with the code, do you have to restrain the branch lines within the grid according to 9.3.6?   

RE: Restraint of Branch Lines

It depends.  You may not dismiss branchline restraint just because the mains attached are braced.

What size are the branchlines?  How long is the run between the mains?  How are the branchlines hung, ie, how long is the hanger assembly?

 

Fire Sprinklers Save Lives.
Can You Live Without Them?
 

RE: Restraint of Branch Lines

(OP)
The branch lines are 2" the mains are 3" and 4"

The length of the branch lines between the mains is approximately 200'-0"

The branch lines are hung 21" below the deck with a top beam clamp, 3/8" A.T.R. and a hanger strap.  

RE: Restraint of Branch Lines

Based on this information, YES, you must provide branchline restraint for the 2-in. branchlines.

Fire Sprinklers Save Lives.
Can You Live Without Them?
 

RE: Restraint of Branch Lines

(OP)
Thank you.  I just spoke with the local AHJ and he is in agreement.  I appreciate your time.

Amanda

RE: Restraint of Branch Lines

Don't forget to verify that your rods meet the l/r requirement of not exceeding 400.  3/8" atr with a vertical dimension of 21" installed on a 45° angle will just barely be under 400 for the l/r value.  If you increase that length at all, you are going to have to go to 1/2" atr.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
 

RE: Restraint of Branch Lines

Wire is another option.

Fire Sprinklers Save Lives.
Can You Live Without Them?
 

RE: Restraint of Branch Lines

(OP)
We use the wire option... It seems to work the best at the cheapest cost material/labor.

RE: Restraint of Branch Lines

(OP)
When laying out the branch line restraints along branch lines that are part of a grid, do you space the restraints from one head onward, or do you consider the connection to the main at both ends the end of a line and both heads at the "end" need to be restrained?   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources