Hello,
I am trying to calculate the % voltage drop and figure out the best approach to the scenario below
I have a SCE Overhead line 16.5KV feeding a transformer which steps the voltage down to 480V which then supplies a control panel about a 1000 feet away. From the panel, we have a firewater pump(150P) connected about 30 feet away. The FLA is 180 and LRA is 1085. Starting power factor is 30 percent and also we assuming normal impedance for the transformer at 5.75%.
I am having a hard time finding the voltage drop given the conditions. Also, I need to know if the 300KVA transformer is viable for the application taking into account the percent of nameplate min is 85%. Please can someone help me figure this out. Currently, I have found applications showing calculations without taking into account the distance. However, this is not accurate considering the 1000'. Please share your comments. Appreciate any help provide
Note: I need to justify backing use of the 300KVA transformer. SCE believes a 150KVA transformer should work fine but I feel this may not be the case considering a distance of a 1000'
I am trying to calculate the % voltage drop and figure out the best approach to the scenario below
I have a SCE Overhead line 16.5KV feeding a transformer which steps the voltage down to 480V which then supplies a control panel about a 1000 feet away. From the panel, we have a firewater pump(150P) connected about 30 feet away. The FLA is 180 and LRA is 1085. Starting power factor is 30 percent and also we assuming normal impedance for the transformer at 5.75%.
I am having a hard time finding the voltage drop given the conditions. Also, I need to know if the 300KVA transformer is viable for the application taking into account the percent of nameplate min is 85%. Please can someone help me figure this out. Currently, I have found applications showing calculations without taking into account the distance. However, this is not accurate considering the 1000'. Please share your comments. Appreciate any help provide
Note: I need to justify backing use of the 300KVA transformer. SCE believes a 150KVA transformer should work fine but I feel this may not be the case considering a distance of a 1000'






RE: Backing of Use of 300 KVA transformer
See attached. Looks like about 79% voltage at the motor - this will depend on the feeder size. I assumed 2-250 kcmil per phase (copper).
RE: Backing of Use of 300 KVA transformer
Thank You. Is the 1000' ft incorporated in the load flow diagram? Is there a way to do these calculations by hand. I would appreciate it if you could share that.
RE: Backing of Use of 300 KVA transformer
This can be done by hand. You need to create an impedance diagram including:
Utility impedance
transformer impedance
cable impedance
impedance of motor at locked-rotor.
It's much easier if you use the per-unit system and put everything on the same impedance base. The IEEE Red Book should cover this pretty well.
Voltage drop calculations are, by nature, iterative. The current into the motor depends on the voltage at the motor which depends on the current. When doing it by hand, some trial and error is required.
I'd guess there are some on-line resources that can help with this calc at no cost.