NFPA 20 (Jockey Pump Capacity)
Other than the method of taking the 1% pressure capacity of fire pump to calculate the jockey pump pressure capacity, is there any calculation method on how to size its pressure capacity. Also, what method should I used in order to size the flow capacity of the Jockey pump.thanks
RE: NFPA 20 (Jockey Pump Capacity)
Given this, for a 500 gpm rated pump, you would size your pressure maintenance pump with ~5 gpm capacity.
The jockey pump should never have a capacity greater than the flow of one sprinkler head.
In terms of pressure, NFPA 20 2010 4.25.3 states "Pressure Maintenance pumps shall have discharge pressure sufficient to maintain the desired fire protection system pressure."
Here's a rule of thumb I use for setting controller pressure points:
Fire Pump stop point is churn pressure + city static
Jockey start is Fire Pump Stop - 10 psi
Fire Pump Start is Jockey start - 5 psi
So, your jockey pump has to at least be able to maintain the fire pump stop pressure.