what is limitation for height of masonry wall if it's single story.
can i use 8-10 in wall for 25-30ft high. It's load bearing wall.
 

RE: wall height

Normally, the limiting H/t ratio is 35, so you are looking at a 10" wall for 25 feet, and a 12" wall for 30 feet.  

However, if my memory serves me right, I believe that the PCA Slender Wall Design brochure allows ratios up to 50.  There are other design considerations too, plus it's been a while since I did this, the code has probably changed, and my book is packed away.

Mike McCann
MMC Engineering

 

RE: wall height

Depending on the code... in our locale, the maximum h/t for bearing walls is typically 18 or 20 based on the actual wall thickness, not nominal thickness... this limits your 10" block wall to approx 16'...

Dik

RE: wall height

Reference - ACI 530-05   
Chapter 2- Allowable Stress Design of masonry - Columns: ratio between effective height and least nominal dimension shall not exceed 25. There are no h/t limits specified for walls.

Chapter 5 - Empirical Design of Masonry : Section 5.5.1
     Type of Construction                         l/t or h/t
   Bearing Walls
      solid / fully grouted                           20
      All other                                          18
    t is the nominal thickness of wall.
     
   

 

RE: wall height

(OP)
if i will follow method based on chapter 2 and design 8 inch interior bearing wall which can take 1 klf  load and out of plane seismic load,  then is this possible to use?

 

RE: wall height

Doesn't matter... the height intended is too much... as noted and as based on DST's comments, you shouldn't be going higher than about 16' with 10" block... You can reinforce it and design it using code portions for slender walls, but you will not achieve a 25' height... You need reinforced pilasters or structural steel to provide the lateral support.

Dik

RE: wall height

I don't see where DST said the height was too much. There is no h/t limit if you're going to design per ACI 530 Chapter 2. Forget the empirical design of Chapter 5. However, that being said, you may get 10" to work for 30', but not 8". The seismic and/or wind stresses would probably be too high even if the wall is significantly reinforced.

RE: wall height

...go for it spats...

I've used engineered masonry long before it was codified... both for slender walls and for twenty storey apartment buildings.  It's going to be really difficult to get the last couple of feet of the 30' height to work... and, I'd probably leave the scaffolding in place... even if no seismic or wind...

Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources