Capacitive Pressure Transducer
Capacitive Pressure Transducer
(OP)
I'm using a Setra Model 264 Low Differential Pressure Transducer to measure pressure differences in a water manometer. However, I am getting outputs in voltage using a voltmeter and want to know how to convert these voltages to pressure in mm H2O.





RE: Capacitive Pressure Transducer
RE: Capacitive Pressure Transducer
Gosub MintJulep.
RE: Capacitive Pressure Transducer
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize
RE: Capacitive Pressure Transducer
Good on ya,
Goober Dave
RE: Capacitive Pressure Transducer
Need the voltage range and the pressure range. Here's an example:
Assume you are using the standard voltage output of 0 - 5 VDC.
And let's say the range is 0 - 2.5 in. wc.
If you are reading 2 volts on your meter then you would convert as follows:
(2 volts x 2.5 in. wc.)/ 5 VDC = 1 in. wc.
I noticed you asked for mm, so I'll let you do the conversion.