I have one mechanical unit which is suspended from steel roof framing. how to support unit with steel framing. unit weight is 500 lb.
Thank you
Thank you
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: suspended unit
RE: suspended unit
what is best way to support.
RE: suspended unit
Don't forget - two fat boys weigh about 500 lbs.....Not usually a big problem UNLESS it wasn't designed very well or is quite old??
RE: suspended unit
1. Yes - mechanical units are usually suspended from roof framing with four threaded rods (size depends on the unit's weight).
2. We typically run a steel angle spanning between the rods. Two angles at either end of the unit to support the unit.
3. The rods can be connected to the roof framing in various ways - depends on the type of roof.
4. Your design checks:
a) Angle size required to span between rods.
b) Rod diameter required to support the load.
c) Rod fastening system at the roof members.
d) Check roof members for overall loading of the unit (shear, flexure, connection to other supports).
e) Check local problems with the rod concentrated load on the roof members (i.e. steel joist bottom chord bending)
f) Design required lateral braces if required due to seismic area.
g) Check deflection of roof under new load - ponding/drainage now an issue?
RE: suspended unit
Hanging small mechanical equipment is similar to trapezes for pipes. There are a number of companies that provide information and details for trapezes (Unistrut, Powerstrut, B-Line, Tolco, Mason Industiries, etc.).