RESISTIVE LOAD BANK

RESISTIVE LOAD BANK

RESISTIVE LOAD BANK

(OP)
Hi all,

we want to load test a generator to confirm the operation of the generator voltage governor and the excitation circuit. is a resistive load bank is enough or an inductive load bank is required for this purpose?
thanks

RE: RESISTIVE LOAD BANK

Resistive is fine. The only time I would use inductive load banks would be on powerplants.  

RE: RESISTIVE LOAD BANK

If there are large inductive loads that require significant reactive power be developed you may want to look at an inductibe bank or alternatively load the generator to near its KVA rating with the resisy=tive bank to ensure the voltage regulator and exciter can support nameplate amps.

RE: RESISTIVE LOAD BANK

(OP)
thanks for your input.
my question is when you use a resitive load bank, how is the Vf voltage and If current (field voltage and current) vary from no load state to full load state. I would imagine the field voltage and field current from AVR would be the same from the no load to full load states since it is a resistive load. what do you think?

thanks

RE: RESISTIVE LOAD BANK

No, not constant at all. The excitation has to make up for resistive and inductive voltage drop in the generator windings. There is also magnetic influence of the load current on the air gap flux, which needs to be compensated for by increased excitation current (and, of course, voltage).

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: RESISTIVE LOAD BANK

The excitation voltage and current may approximately double from no load to full load on a diesel generator.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: RESISTIVE LOAD BANK

Depends on your application and expected use. If this is a single island mode operating unit, like a standby, and your loads are well within the rated power factor of the generator, then a resistive test will likely be fine.

However, do you need to qualify droop or line drop compensation? Or does the end user or AHJ require testing that deomstrates not only full load real power but also full kVA load from the tail end?  If so then likely a resistive/reactive load test will be required.

The last few years I worked for a CAT dealer, about 25% of the standby generator set sales/startup jobs required a full load test at nameplate power factor to satisfy end user or contract requirements. Saw this increasing over the years.

On shipboard diesel electric system units we always did a resitive/reactive load bank test as required by the marine regulatory agencies and to make sure the controls and protections operated as expected.

So my best answer is, "depends".  More details on your unit, application and if you have any regulatory or contractural requirments can get you a more definate answer.

Hope that helps.

Mike L.

RE: RESISTIVE LOAD BANK

(OP)
thanks for the replies.
there is no requirement for kva testing. the single unit generator is used as an emergency power source and as soft load transfer during scheduled maintenance.
i wanted to confirm that the operation of  speed and voltage regulation controllers  with  resistive load bank.

thank you  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources