we want to load test a generator to confirm the operation of the generator voltage governor and the excitation circuit. is a resistive load bank is enough or an inductive load bank is required for this purpose?
thanks
we want to load test a generator to confirm the operation of the generator voltage governor and the excitation circuit. is a resistive load bank is enough or an inductive load bank is required for this purpose?
thanks





RE: RESISTIVE LOAD BANK
RE: RESISTIVE LOAD BANK
RE: RESISTIVE LOAD BANK
my question is when you use a resitive load bank, how is the Vf voltage and If current (field voltage and current) vary from no load state to full load state. I would imagine the field voltage and field current from AVR would be the same from the no load to full load states since it is a resistive load. what do you think?
thanks
RE: RESISTIVE LOAD BANK
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: RESISTIVE LOAD BANK
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: RESISTIVE LOAD BANK
However, do you need to qualify droop or line drop compensation? Or does the end user or AHJ require testing that deomstrates not only full load real power but also full kVA load from the tail end? If so then likely a resistive/reactive load test will be required.
The last few years I worked for a CAT dealer, about 25% of the standby generator set sales/startup jobs required a full load test at nameplate power factor to satisfy end user or contract requirements. Saw this increasing over the years.
On shipboard diesel electric system units we always did a resitive/reactive load bank test as required by the marine regulatory agencies and to make sure the controls and protections operated as expected.
So my best answer is, "depends". More details on your unit, application and if you have any regulatory or contractural requirments can get you a more definate answer.
Hope that helps.
Mike L.
RE: RESISTIVE LOAD BANK
there is no requirement for kva testing. the single unit generator is used as an emergency power source and as soft load transfer during scheduled maintenance.
i wanted to confirm that the operation of speed and voltage regulation controllers with resistive load bank.
thank you